T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
35 63-4368
Table 21. T7350H Network Variable Summary. (Continued)
Nv Name L
ONSPEC™ Ref Name Class Description
nciRcvHrtBt Controller Receive Time CONFIG Receive heartbeat time (seconds) for all failure detect heartbeat
network variables in this node.
0: Disable failure (Default).
300: Typical value in Honeywell system.
nciSetpoints Setpoint Config CONFIG Heating and Cooling SetPoints in Celsius engineering units.
Occupied cool set-point.
23.9 C: (Default)
Standby cool set-point.
25.6 C: (Default).
Unoccupied cool set-point.
29.4 C: (Default).
Note:
It is required that:
UnoccCl>=OccCl>=OccHt+1.11 C.
UnoccCl>=StdByCl>=StdByHt+1.11 C.
If the above criteria is not met, then the nciSetpoints received over
the L
ONWORKS network will not be accepted, and all the current
controlling set points will be restored from the thermostat.
Occupied heat set-point.
21.1 C: (Default).
Standby heat set-point.
19.4 C: (Default).
Unoccupied heat set-point.
12.8 C: (Default).
It is required that:
UnoccHt<=OccHt<=OccCl-1.11 C.
UnoccHt<=StdByHt<=StdByCl-1.11 C.
If the above criteria is not met, then the nciSetpoints received over
the L
ONWORKS network will not be accepted, and all the current
controlling set points will be restored from the thermostat.
nciSndHrtBt Controller Send Time CONFIG Send heartbeat time (seconds) for all Guaranteed periodic update
heartbeat network variables in this node.
0: Disable periodic update (Default).
55: Typical value in Honeywell system.
nroPgmVer Program Version CONST The Honeywell program identifier and subbase firmware version
number.
nroT7350Ver T7350 Version CONST Detailed T7350 cover assembly firmware version information.
nviApplicMode Application Mode In IN Thermostat System mode switch:
0: HVAC_AUTO
1: HVAC_HEAT
3: HVAC_COOL
6: HVAC_OFF
8: HVAC_EMERG_HEAT
Others: Considered to be HVAC_AUTO.
Failure detect and mains power up value: HVAC_AUTO.